Please let me clarify my previous entry on receptacles.
I have been ask to drop out of a 60 amp disconnect with two SO pigtails. Both with 55-amp twist lock receptacles on them.
Added, the receptacle amps are 110, but the loads will not run at the same time and they run around 30 amps each. My wire will be rated for 60 amps and I will use 50 amp fuses.
New Lugs rated for two conductors to replace the ones on the disconnect would be great if I could find them. Distribution blocks would work well but I did not want to add any more boxes unless I had to.
Question 1) Even though I am protected at 50 amps does this arrangement comply with the code?
Question 2) If compliant, what is the best way to tap these wires.