I would look at Raychem GelCaps over a crimp ring and bolted connection. The GelCap is filled with a re-enterable silicone gel that keeps the water out.
I see they have a new version of scotchcoat out that doesn’t require me to bury the guy that spills it on himself. GB has a version that seems to work well too.
water-tight splices/connections are the way to go
We wouldn't get by with that.
We did a fair bit of work for water companies including submersibles. The motor leads were usually short straight out of the motor so connection boxes were generally down the well. We wouldn't be permitted to use splices, waterproof or otherwise. Terminals were DIN rail in an IP66/67 box with CW glands for cable entry and exit.Wet location wire and splices are readily available, but they don't let you use them in underground boxes or vaults over there in the UK?
In a handhole enclosure you basically must use items that are otherwise direct bury suitable. Many cases even the enclosure will silt in over time. The cover just makes it easier to know where the connections are without the need for locating equipment. Been to places where cover gets buried over time and still need to probe around to find it.We did a fair bit of work for water companies including submersibles. The motor leads were usually short straight out of the motor so connection boxes were generally down the well. We wouldn't be permitted to use splices, waterproof or otherwise. Terminals were DIN rail in an IP66/67 box with CW glands for cable entry and exit.
These were customer/consultant specs. I don't know whether the regs mandated them.
I use them for motor connections where they will fit in the motor junction box. We would typically use rubber and plastic tape on those connections in the past. I find the GelCaps to be better, and cheaper than taping.I haven't used these, but this would be the way to go.