Talked the customer into using one switch for all the lighting. So a 2 gang switch plate with a toggle switch blank for my fubar and we're rollin' again!
Are you guys confused with maybe 408.8(B):
I sure hope you can install separate switches in separate boxes, otherwise all the switches in a particular building would all have to be in same box - sounds pretty inconvenient for the user in most cases.
I don't think this section would apply to a switch rated for 480 volts unless there is one that is considered a general purpose snap switch and not a manual motor controller. Only ones I have seen are called motor switches or something of that nature and are rated for 600 volts, 1, 2 or 3 pole.
Can't use 120/277 switch. Voltage across switch when open will be 480 volts.
Okay, I must be on the 2008 code because I do not have 408.8(B). I think you meant 404.8(B)? I knew about that reference, how does that apply to installing 1 switch in one box and one switch in another? Which was my original suggestion.
jA check of the UL White book will reveal that contactors marked as 'definite purpose' contactors have not been evaluated for lighting loads. Only units marked as 'lighting contactors' are.
Indeed, there are a whole variety of uses for which the 'definite purpose' contactor has not been evaluated. It appears that 'definite purpose' really means it's not good for much at all!
I don't make this stuff up, I often think a lot of it is a crock, and it should surprise no one that engineers are terrible authors .... but facts are facts.
A check of the UL White book will reveal that contactors marked as 'definite purpose' contactors have not been evaluated for lighting loads. Only units marked as 'lighting contactors' are.