Current project is scheduled for 480V, 3 phase. The project loads are two 75HP pumps, one 40HP pump and lighting loads. The 75HP pumps are scheduled to operate on variable frequency drives, and the 40HP pump is scheduled to be across the line.
The utility company has gone from a $55,000 budget to a $120,000+ budget for 480 volt, 3 phase. They offer 480 volt single phase for no cost. I do not see any problems with 480 volt, single phase service and using derated VFD to get 480 volt 3 phase to the 75HP, and 40HP motors.
The project has a 350KW generator scheduled for instalation. It is a 12 lead generator. I talked with the factory about connecting it 480 volt single phase, and they said what? The vector analysis is the same for a 120/240 volt single phase 12 lead generator. I asked them to change the generator to 480 volt, single phase and they said that they don't make a single phase generator that big. They also said that they don't make a 480 volt, single phase generator either.
That started me thinking is 480 volt single phase service even used? I found a utility company here in Texas that supplie it, put only for municipal and highway lighting.
I hate to get a 240 volt single phase service convert everything over to 240 volt, 3 phase and eat all of the equipment that cant be returned.
Can't find anything in NFPA 70 2008. I don't understand what will be wrong with it, can anyone convice me either way?
Most of the equipment is either shipped or on the job.
The utility company has gone from a $55,000 budget to a $120,000+ budget for 480 volt, 3 phase. They offer 480 volt single phase for no cost. I do not see any problems with 480 volt, single phase service and using derated VFD to get 480 volt 3 phase to the 75HP, and 40HP motors.
The project has a 350KW generator scheduled for instalation. It is a 12 lead generator. I talked with the factory about connecting it 480 volt single phase, and they said what? The vector analysis is the same for a 120/240 volt single phase 12 lead generator. I asked them to change the generator to 480 volt, single phase and they said that they don't make a single phase generator that big. They also said that they don't make a 480 volt, single phase generator either.
That started me thinking is 480 volt single phase service even used? I found a utility company here in Texas that supplie it, put only for municipal and highway lighting.
I hate to get a 240 volt single phase service convert everything over to 240 volt, 3 phase and eat all of the equipment that cant be returned.
Can't find anything in NFPA 70 2008. I don't understand what will be wrong with it, can anyone convice me either way?
Most of the equipment is either shipped or on the job.