strawburner
Member
- Location
- Central Kansas
I need to run 2600ft. of underground single phase 100amp service to a rural shed and feedlot. The POCO will set a 480 volt single phase trans. at a minimal cost I would then step down the voltage at the load to 120/240 volts. Here is what I am proposing to do after doing the voltage drop calculations. Use AL 500kcmil with 350 neutral with a 25KVA step down transformer at the load. This being the first time I am doing this I am wondering if this will this work satisfactorily?