Got an issue and need some input. I have been in electrical for 30 years and this is first time I have seen this voltage from the utility. I am a project manager for the issue below and I hold a master license in Florida.
I am building a small 100 amp 240/480 volt single phase service for temporary construction power and will be installing a 480 to 120/240 transformer to power the GC's construction office. I had discussed the voltage with the FPL (Florida Power and Light) engineer prior to designing the service and was told their transformer was a 240/480 output so that is how we have built our service.
I have a single phase meter socket and then a 2 pole fused 100 amp disconnect switch for my main. We had ran our service conductors from the utility transformer to our meter with 3#1 aluminum (I believe but cannot be sure since I am at home at this time) , 2 hot lines and one neutral.
FPL came out to hook us up today and they realized that they have a 240/480 transformer, but it has been modified or jumpered to produce 480 on one line to ground. FPL sees that we have 3 conductors and says "sorry, we cannot hook you up" because we (FPL) do not have 2 hot legs with 480 between them and 240 to ground. My foreman who is present with the power company is very confused with a 480 volt single line to ground service that he agrees there is a problem and FPL leaves.
My foreman calls me right after FPL leaves and explains the issue to me, but not ever having heard of this single line 480 to ground power from utility, I was scratching my head and wondering if it will work if we just eliminate one of the lines that we have pulled to the utility transformer.
So question is, if FPL does not have an issue, could I bring one line and one neutral (or grounded conductor) to my meter and then go from meter to fused disconnect with same (one line and one neutral) and then feed a 50 KVA single phase transformer (it is a Square D EE50S3H) with this 480 volt tied to H1 and H4 (which are the points to connect the 480 volt) and have it work fine? My man in field has connected a thousand transformers with 480 (line to line), but this is freaking him out that the 480 is one line to neutral and I have not run into this either so I cannot say that it will or will not work, but in my mind it should work just fine.
Also, being unusual to me I started to question if the 100 amp fuse on the single line would be adequate since we had figured we would be using 2 hot legs to get 480 but we now have only one single hot leg. The math says it should be fine, but again very unusual system and just second guessing myself.
Please give my your thoughts if you believe this will work just fine or not.
I am building a small 100 amp 240/480 volt single phase service for temporary construction power and will be installing a 480 to 120/240 transformer to power the GC's construction office. I had discussed the voltage with the FPL (Florida Power and Light) engineer prior to designing the service and was told their transformer was a 240/480 output so that is how we have built our service.
I have a single phase meter socket and then a 2 pole fused 100 amp disconnect switch for my main. We had ran our service conductors from the utility transformer to our meter with 3#1 aluminum (I believe but cannot be sure since I am at home at this time) , 2 hot lines and one neutral.
FPL came out to hook us up today and they realized that they have a 240/480 transformer, but it has been modified or jumpered to produce 480 on one line to ground. FPL sees that we have 3 conductors and says "sorry, we cannot hook you up" because we (FPL) do not have 2 hot legs with 480 between them and 240 to ground. My foreman who is present with the power company is very confused with a 480 volt single line to ground service that he agrees there is a problem and FPL leaves.
My foreman calls me right after FPL leaves and explains the issue to me, but not ever having heard of this single line 480 to ground power from utility, I was scratching my head and wondering if it will work if we just eliminate one of the lines that we have pulled to the utility transformer.
So question is, if FPL does not have an issue, could I bring one line and one neutral (or grounded conductor) to my meter and then go from meter to fused disconnect with same (one line and one neutral) and then feed a 50 KVA single phase transformer (it is a Square D EE50S3H) with this 480 volt tied to H1 and H4 (which are the points to connect the 480 volt) and have it work fine? My man in field has connected a thousand transformers with 480 (line to line), but this is freaking him out that the 480 is one line to neutral and I have not run into this either so I cannot say that it will or will not work, but in my mind it should work just fine.
Also, being unusual to me I started to question if the 100 amp fuse on the single line would be adequate since we had figured we would be using 2 hot legs to get 480 but we now have only one single hot leg. The math says it should be fine, but again very unusual system and just second guessing myself.
Please give my your thoughts if you believe this will work just fine or not.