The 480 volt single line is not jumping to both terminals. The one 480 leg would be on either H1 or H4 and the neutral would be on the other. I think it would work but after a phone call with Square D today, they say it won't work, but I think because they do not want the liability.
POCO came out and explained to us today that they have no issue with it but in order for the electronic meter to work we would need to install a jumper between the neutral and the 2nd (normally hot leg) line terminal of the meter so it would receive power.
Since Square D has decided to say no to us connecting this, we opted to also say no to protect ourselves from liability as well.
GC will now be paying POCO to install a 240/480 pad mount transformer immediately adjacent to the 480 single line transformer. This way we can just have them connect what we have and move on from this mess.
I about brought up the meter issue before also.
I was wondering how the meter would ever work with only 1 leg utilized.
Oh well,
Sounds like they're going to get you fixed up.
JAP>