Hello, we have a property that one had a laundromat. I am not a electrical expert but have basic understanding. They had three 240v panels. Two of the service panels are set up with 3 hots and a neutral and I believe are 240v high leg 3ph Delta panels. There are 3 phase breakers on the A-B-C slots, 240 on A-C slots, and single 120's but not on the B slots. A third panel has 2 hots and 1 neutral and it looks like it is setup for single phase 120 and 240 breakers. We have a new 460v Lennox HVAC unit on the roof and we need heat now in Chicago. Other than 1) new expensive 480 service just for the HVAC and 2) a 240v to 480v step up transformer, is there any way to get 480v 3ph power? I doubt it, but some people involved insist that you can so I am asking.Two electricians said no but they are not the brightest stars. And if a transformer is the only way, which of the following is best for a HVAC unit with a sophisticated control board:
1) 240v Delta to 480v Delta with isolation
2) a multi tap using 240v to 480v no isolation But we like for future proofing and having options
3) 240v Delta to a 480v Wye
The unit draws little less than 30 amps - 26A with 24v transformer step down circuits. It does not specifically mention any type of 480v 3 ph like120v or 240v legs or 277v. However the blower motor has an inverter as I understand it and the more balanced load the better. Yes, I have been calling
Lennox technical for weeks but because of Covid and very limited staff, no one answers the phone! Any help ASAP is greatly appreciated, thanks in advance. I tried to attach a photo of the HVAC name plate but it will not load.
1) 240v Delta to 480v Delta with isolation
2) a multi tap using 240v to 480v no isolation But we like for future proofing and having options
3) 240v Delta to a 480v Wye
The unit draws little less than 30 amps - 26A with 24v transformer step down circuits. It does not specifically mention any type of 480v 3 ph like120v or 240v legs or 277v. However the blower motor has an inverter as I understand it and the more balanced load the better. Yes, I have been calling
Lennox technical for weeks but because of Covid and very limited staff, no one answers the phone! Any help ASAP is greatly appreciated, thanks in advance. I tried to attach a photo of the HVAC name plate but it will not load.