Something else not mentioned - is this replacing something of similar electrical load ? If not can your service handle the additional load?
That unit may need 30 amp circuit @ 480 volts, but should need about 70 amp circuit if same capacity @ 208 volts. The feed to the transformer still draws that same amount from the 208 input.
If service needs upsized you are spending some $$ anyway.
That unit may need 30 amp circuit @ 480 volts, but should need about 70 amp circuit if same capacity @ 208 volts. The feed to the transformer still draws that same amount from the 208 input.
If service needs upsized you are spending some $$ anyway.