winnie
- Springfield, MA, USA
- Electric motor research
I want to argue about the applicability of 250.2(B)2...but that would really derail this thread. However thinking on the issue I came up with a potential 'gotya' in the current proposed solution.
Say the supply is a corner grounded delta, and the new delta-wye transformer is properly neutral point grounded. ?The voltage between supply conductors could be as high as 757V (going from one of the original ungrounded delta conductors to one of the newly derived wye conductors). The line-line voltage seen by the heaters will be 480V or 277V as intended, so this high 'apparent' shouldn't impact the function of the intentional circuits.
Where this voltage comes into play is for things like insulation: Will the insulation system in the machine and field wiring be happy with this voltage? Are there contactors in the machine that might have trouble with this voltage on adjacent poles? Do conductors land on terminal blocks designed for lower voltages?
If the supply is ungrounded, will a ground fault elsewhere in the plant cause transient damaging voltages in this machine?
Which simply goes to emphasize the importance of iceworm's questions.
-Jon
-Jon