A couple of issues with some of proposals: I'm not pointing out that anybody is wrong, just suggesting there is a lot we don't know.
I don't think a z-z derived neutral is a good choice. There is no isolation, it will act as grounded neutral for the entire system. And we don't know what the existing is:
- 480 grounded Y, neutral brought to the first disconnect.
- 480 HRG
- 480 ungrounded D
- Corner grounded D
We have no clue what system faults we could induce. If we are to suggest a z-z derived neutral, it should come with a mandate to review the existing system. With 1300A of spare capacity this is a non-trivial system. Easily could be 2MVA or bigger.
Connecting the 277V heaters without a neutral:
This only works if the 277V heaters are switched in banks of three. Are they? Don't know.
(
edit to add) kwired is discussing these.
Using two feeds, one 480/277 grounded Y and one 480V 3W unspecified grounding could easily require internal wiring changes.
SF - Your going to have to get the book/wiring diagrams out.