I’m bidding a large ground mount solar job with a standby generator, and the existing service is throwing me for a loop. I’m used to either 120/240 service or 480/277 3ph service.
The existing meter from the power company is a 480/277 3ph meter, fed into a fused disconnect, where to 3/0 conductors and a ground exit and travel approximately 800ft to a gutter with three disconnects, all ultimately feeding three 50kva single phase 480v primary to 120/240 secondary dry transformers, placing the entire load on two phases. For load balancing, I thought that was a no go?
I was planning on using an SMA 50kw TriPower inverter, which is 480v three phase, and we could run that back to the meter to grab the missing phase conductor; however the load imbalance would result in exporting on the unused phase 100% of the time, and importing via the other two phases to make up the difference. To keep it balanced, the other option would be to back feed at 120/240 and use a single phase transformer and tap the existing feeders and keep it all on the existing phase. More complicated and can’t use the built in three phase voltage configuration of a tripower.
The same challenge exists with the generator transfer switch, and third unused phase. If the generator were after the existing transformers, that wouldn’t be that big of a deal, but they’re asking to cover the entire property, so I need to be on the 480v side — which would again place all of the load on two of the three phases. I haven’t seen a 480v single phase option from Generac.
My business is nearly entirely residential solar and electric, I rarely deal with 3ph so pardon my lack of intelligence, and thank you for your wisdom and I appreciate your help.
The existing meter from the power company is a 480/277 3ph meter, fed into a fused disconnect, where to 3/0 conductors and a ground exit and travel approximately 800ft to a gutter with three disconnects, all ultimately feeding three 50kva single phase 480v primary to 120/240 secondary dry transformers, placing the entire load on two phases. For load balancing, I thought that was a no go?
I was planning on using an SMA 50kw TriPower inverter, which is 480v three phase, and we could run that back to the meter to grab the missing phase conductor; however the load imbalance would result in exporting on the unused phase 100% of the time, and importing via the other two phases to make up the difference. To keep it balanced, the other option would be to back feed at 120/240 and use a single phase transformer and tap the existing feeders and keep it all on the existing phase. More complicated and can’t use the built in three phase voltage configuration of a tripower.
The same challenge exists with the generator transfer switch, and third unused phase. If the generator were after the existing transformers, that wouldn’t be that big of a deal, but they’re asking to cover the entire property, so I need to be on the 480v side — which would again place all of the load on two of the three phases. I haven’t seen a 480v single phase option from Generac.
My business is nearly entirely residential solar and electric, I rarely deal with 3ph so pardon my lack of intelligence, and thank you for your wisdom and I appreciate your help.