gar
- Ann Arbor, Michigan
- EE
201209-1044 EST
Starting with post #1.
I would not call a single wire a phase, but some do. It takes two wires to have a phase.
From the three wires of what I think is being described in post #1 we have most of a 3 phase wye source, two phases of the source. The one wire being called ground is not required to be grounded to analyze the circuit operation. This wire is the neutral of a balanced 3 phase wye, but as applied here is not really a neutral.
From this partial three phase wye you can easily obtain an open delta with two transformers. That is how my shop building is driven. This type of loading is all around me.
I believe in the first post is described three single phase transformers with their primaries connected in parallel, all connected across one 480 V phase of the source. Nothing wrong with this, if that is what the power company expects.
The transformer for my home is a single phase transformer connected to two wires of a three phase delta on the pole. Power distribution in my area is 3 phase delta, three wires on the pole. No neutral or ground for the primary distribution. However, it is probably driven by a 3 phase wye at the substation to provide a reference to earth.
As you go down the poles in my area you will find that different distribution transformers are on different phases to evenly distribute load back at the substation.