tryinghard
Senior Member
- Location
- California
I have a 400A 480V 3PH 3W delta service to a service disconnect. This service disconnect is a 480V 4W ? A, B, C phases & EGC ? that feeds a transfer switch and an MCC each 480V 4W (A, B, C phases & EGC), the generator set is also 480V 4W.
I am concerned about not having a grounded conductor with the service; will a downstream ground fault be impeded without the service grounded conductor? In other words will a ground fault operate any breaker just a quick with or without the service grounded conductor?