Only if he ever gets it to run long enough.
Only if he ever gets it to run long enough.
Don't we use the table values instead of the marked values for the current?
You use the table amps for sizing the circuit components (conductors and short circuit protection). You use the nameplate/actual amps for protective devices operation time and coordination.Don't we use the table values instead of the marked values for the current?
I don't see how it's a grey area. 430.6(A)(1) is very clear.Depends. NEC refers to FLC and FLA but does not define them. So it’s a grey area.
Practice with some is to size the starter and maybe breaker or fuses by table but overloads by name plate. Others say all protective devices must use name plate.
430.6 applies to conductor sizing and SC protection and requires use of the tables.I don't see how it's a grey area. 430.6(A)(1) is very clear.
What part of the starter label "USE FUSES ONLY" allows a breaker anyway?I ran the circuit to the machine and installed a 90amp Siemens BQD series breaker in the load center.
And it shows a 200A max fuse on the front of the overload relay.What part of the starter label "USE FUSES ONLY" allows a breaker anyway?
trouble-makerWhat part of the starter label "USE FUSES ONLY" allows a breaker anyway?
Use‘A’ on the label not ‘SFA’.
Unless, you are a well driller. Then you can use whatever you choose.
Seems like a lot of the submersible pump manufacturers design their pump ends to load the motor into the service factor amperage.
Seems like a lot of the submersible pump manufacturers design their pump ends to load the motor into the service factor amperage.
Industrial air compressors are the same way.
They are relying on duty cycle. Seen a lot of plants that have so many leaks or add so much equipment they set the pressure switch beyond what it will ever reach so it hits 100% duty. Only takes a day or two to make a motor sale.
Good catch!What part of the starter label "USE FUSES ONLY" allows a breaker anyway?
Ages ago, the NEMA definition of "Service Factor" used to mention it being suitable for a "intermittent" use, without ever actually defining what "intermittent" meant. Somewhere a couple of decades ago, NEMA amended it to remove all reference to SF having a time frame associated with it, so OEMs have been using that to run motors into the SF continuously. What NEMA says now though is a bit more namby-pamby...'I've seen irrigation well motors that have run into the SFA for decades. Not today's bare minimum material high efficiency motors.
A motor operating continuously at any service factor greater than 1.0 will have a reduced life expectancy as compared to operating at its rated nameplate horsepower. Insulation life and bearing life can be reduced by the service factor load.
No we don’t. Our units are designed to run flat out at 100% load at 110% of motor nameplate HP.
That’s normal throughout the industry.
Good catch!
A lot of people miss this issue. Some motor control equipment mfrs, especially those who do not make breakers, do not get their starters and OL relays UL listed behind breakers, they only use fuses in order to pass the UL testing because that's cheaper and easier for them. That then falls upon the installer to ONLY use fuses in the installation. So technically even if you were to feed it from a 200A breaker in a panel, you would ALSO have to have fuses in series too. That cheap starter isn't as cheap as you thought it was now...
So you operate at 1.10. On a 1.15 SF motor what happens with a 1% voltage unbalance or a 10% overvoltage as per NEMA?