480V circuit in EMT

Status
Not open for further replies.
I imagine you could put medium voltage cable in EMT if you wanted.

Yes

II. Requirements for over 1000 Volts, Nominal

300.37 Aboveground Wiring Methods. Aboveground
conductors shall be installed in rigid metal conduit in intermediate
metal conduit, in electrical metallic tubing, in
RTRC and PVC conduit, in cable trays, in auxiliary gutters,
as busways, as cablebus, in other identified raceways, or as
exposed runs of metal-clad cable suitable for the use and
purpose. In locations accessible to qualified persons only,
exposed runs of Type MV cables, bare conductors, and bare
busbars shall also be permitted. Busbars shall be permitted
to be either copper or aluminum.
 