labigriver
Member
My building has a 277/480v service with solidly grounded neutral at the padmount xfmr (by the utility) and also grounded at the panel by ground rod. This service feeds 277v lighting load, 480v pump motors, 480v hoists, and two 10ton 480v heat pumps. It also serves a three phase 277/480 to 120/208 transformer which feeds office area with 120 volt receptacles, lighting, and kitchen area, etc. The 120/208 transformer neutral (X0) is solidly grounded by ground rod and the neutral and gnd bus in the 120/208 panel are bonded together. This morning we found the surge protectors on all three incoming phone lines blown. Phone company stated the boards in their distribution center were blown out. We found two wires on the 480v fan motor in one of the heat pumps burned really bad and wires melted from terminals but voltage still present on the wires. About this same time someone inside the building connected two gnd points (by coincidence) together with a condutor and drew a very large arc which in turn blew one of the fuses in the heat pump. The heat pumps have only terminals for the three phase conductors and an equipment ground, not a neutral. Is this correct and if so could someone please explain the theory of what happens with a phase to case gnd fault at the heat pump location? Is it possible the heat pumps were designed for a 480v delta instead of what we have? Any assistance greatly appreciated.