Currently quoting a job installing 8 light poles with (12) 150W light fixtures on each pole.
The runs will be fed from two different 480V sources. (4 light poles on one panel and 4 light poles on the other panel)
Just wanting to double check my load calc & conduit fill.
1. Am I right to assume 150W x 12 = 1800W/ 480V = 3.75A at each light pole? If so that means 15A total current on that circuit.
2. With a distance to the furthest pole at 1353’ I should run 4AWG.
3. (5) 4AWG in schedule 40 PVC means I should run 1 1/4” conduit?
4. With a load of 3.75 A at each pole I could run #12 or #10 up each light pole?
Thanks in advance!