This is the lighting spec sheet, the fixtures are J1 300W
assumed a neutral since i was used to running 277V but i realized my mistakeWhy or how did you get (5)?
You left out a 1.73.9,600W/480V = 20A
Like you would a 240v load on 240v. Two lines, no neutral.This being said how do i connect to the fixtures as 480V 3-phase?
Ah i see! ok so to get the current on three phase system i divide by 1.73.You left out a 1.73.
9600 / 480 / 1.73 = 11.56a
Like you would a 240v load on 240v. Two lines, no neutral.
I still think the delta method makes most sense, but nobody said anything about it.
would be much easier to get that 20A breaker vs a 25AYou left out a 1.73.
9600 / 480 / 1.73 = 11.56a
Like you would a 240v load on 240v. Two lines, no neutral.
I still think delta to each pole makes the most sense, but nobody has said anything about it.
Read my post #8 again. You do not need the largest wire all the way to the first pole.Ah i see! ok so to get the current on three phase system i divide by 1.73.
So that being said a 480V 3-pole 20A breaker would be plenty correct?
And my phase conductors would be 6AWG instead of 3AWG?
I'm thinking run #10 between poles 3 and 4, #8 between poles 2 and 3, #6 between poles 1 and 2, and #8 from panel to pole 1 (the home run).First light is 473' away.. so i could technically run #10 to the first pole?
I thought I did, but maybe I just assumed everyone would follow my train of thought.You left out a 1.73.
9600 / 480 / 1.73 = 11.56a
Like you would a 240v load on 240v. Two lines, no neutral.
I still think delta to each pole makes the most sense, but nobody has said anything about it.
Yes. (I haven't confirmed the math)and i could just run #6 all the way to avoid having to buy a bunch of different wire sizes right?
You could, but I wouldn't. The last pole in each run certainly doesn't need wire that large.and i could just run #6 all the way to avoid having to buy a bunch of different wire sizes right?
Bingo.
I may have missed it. Do you agree with me?I thought I did, but maybe I just assumed everyone would follow my train of thought.
Remember, we're talking line-to-line loads, so each light would be connected to two lines.there will be 8 lights on each pole, but could I run them like this?
Light 1. (4) lights on L1, (4) lights on L2
Light 2. (4) lights on L2, (4) lights on L3
Light 3. (4) lights on L1, (4) lights on L3
Light 4. (4) lights on L1, (4) Lights on L2
I agree. Delta is the way to go.I may have missed it. Do you agree with me?
i thin the OP mentioned multiple 2-wire circuits.
8 lights on each pole does not balance evenly across all three phases. In order to balance the run to the first pole as much as possible you need to swap which phase has lesser load on it at three of the four poles. The fourth pole is going to match one other 3 poles for loading of each phase.there will be 8 lights on each pole, but could I run them like this?
Light 1. (4) lights on L1, (4) lights on L2
Light 2. (4) lights on L2, (4) lights on L3
Light 3. (4) lights on L1, (4) lights on L3
Light 4. (4) lights on L1, (4) Lights on L2