So to give everyone an update, we performed the static test on the troubled fan today. The test consisted of performing a polarization index test on the motor. The PI reached a measurement of approximately 1100 mohms (normal is 30,000 mohms) and stayed around that figure for the duration of the 10 minute test. I am in South Carolina, and we have had a lot precipitation yesterday. The room the fan is located in draws in air from outside, so we believe the test results from the static test might just be due to moisture from the last 24 hours. When we attempted the dynamic test the outlet damper didn't open and we noticed a leak in the instrument air line. The motor operated for about 5 to 10 minutes. After this we re-performed the static test with the same results. I thinking we didn't run the motor long enough to burn off the moisture. So tomorrow we plan to repair the instrument air line, and perform a megger test. I am not able to perform a static test, so I am doing the next thing available. Once the instrument air line is repaired we plan to run the motor for at least 3 hours if available, and then perform another megger test. So my question is what is everyone's thoughts on the PI test results, just moisture? Thanks