Hello All.
Thanks for having me here.
I have a Toshiba 7.5hp 460vAC 3PH motor that is wired for Delta run and is showing a ground fault at the 525 VFD.
Isolated the Motor output from the FVD and simulated a run = no issue.
Megger'd the wiring from VFD to Pecker head = good.
Q: I am getting an ohm reading, but not a continuity buzzer from the fluke measuring at T1/12 to ground, T2/10 to ground, T3/11 to ground. It is consistent between all three phase wires - 3.5kohm or so.
Between each other, I'm getting around 3ohms.
I'm yet to break open the tails and test.
Why am I seeing a resistance value as described above?
Thanks all!
Eddie