480V on 600v wire

Status
Not open for further replies.

K2500

Senior Member
Location
Texas
Is 600V rated wire good for 480V? I ask because 480 max. value is about 679V. Do they take that in to acount when they rate the wire?
 
infinity said:
I would assume he's thinking about peak voltage:

Correct, so I figured peak voltage is still voltage.


480sparky said:
Peak voltage of 480 volts is 679 volts. 480 is the RMS value.

Also correct, but my wire doesn't say RMS, Peak or nominal it just says 600V.


benaround said:
benaround 600vac rated wire is good on any system up to and including 600vac.

Wasn't thinking about 600v systems but peak would be 848.66V. Also an unloaded industrial facility could have a line voltage as high as 620V-630V. That may or may not be O.K., but at the very least seems like it would be pushing it.
 
Wire insulation voltage ratings are RMS, as are most all AC devices and systems. So 600V rated wire will handle 600V RMS, which would technically be 849V peak, but I don't know of anyone who thinks in terms of peak voltages with AC.
 
Jraef said:
Wire insulation voltage ratings are RMS, as are most all AC devices and systems. So 600V rated wire will handle 600V RMS, which would technically be 849V peak, but I don't know of anyone who thinks in terms of peak voltages with AC.

I don't know of anyone who thinks in those terms either, but it was enough to get me wondering.
Thanks for the quick replys.
 
K2500 said:
I don't know of anyone who thinks in those terms either, but it was enough to get me wondering.
Thanks for the quick replys.

In the NEC definitions, voltage (of a circuit) is defined as RMS.
 
chris kennedy said:
Where does the .707 come from?
Boeing. :grin:
707-03.jpg
 
Status
Not open for further replies.
Top