Need some help......I have a 3 phase 480V Delta Primary to 208V WYE Secondary dry transformer......however it was hooked up in reverse.....whereas the Incoming Power is 208V and the Outgoing is 480V.....It feeds a 3 phase 4 wire 480 Volt Panelboard.....they installed a neutral wire from the XO terminal, thru a lug on the frame (stripped the insulation in the lug) and terminated it in the 600V fused disconnect, which then feeds a 480V Panelboard. Al other equiment grounds are terminated in lugs on the shell interior. This cannot be a correct installation in my mind.....GE even stated that it's not correct and a neutral cannot be derived from it.
I've researched and read that it can be wired in reverse and I could derive a Neutral from the 480V side and terminate onto H2......this doesn't make sense to me and GE said it could not be done because it is now basically a Delta/Delta TX......the MRI equipment needs a Neutral and it somehow works the way it is wired right now...as long as FPL power is on. There is Generator feeding the building downstairs, but does not feed the MRI off service.....it is located in an meter room on that floor and feed from an MDP downstairs in the Main Electric Room.
This 480V Panel feeds two 3 phase rooftop Chillers and one MRI machine/equipment. The power company has lost B phase to this building's service 4 or 5 times recently.......each time this has happened the Transformer shakes so loud that no one can speak in the office. It has also caused the Equipment ground terminated in the 208V MDP to burn back the insulation. Each time this has happened the people in the office have turned off the Breaker feeding the transformer until the power company fixed it's problem. Then restarting the TX with no issues.
I am planning to install a new 208V primary to 277/480V secondary transformer to at least have the properly rated equipment.......my question is if anyone can lend me some advice as to why the transformer shakes so badly when a phase is lost and why would the equipment ground be carrying amperage and melting under this condition? Is the XO termination lost when the one phase is missing (it typically has been B phase by the way)....My guess is the Neutral feeding the 480V panel from the 208V XO has to be the root of the problem, but I do not know why.
I've researched and read that it can be wired in reverse and I could derive a Neutral from the 480V side and terminate onto H2......this doesn't make sense to me and GE said it could not be done because it is now basically a Delta/Delta TX......the MRI equipment needs a Neutral and it somehow works the way it is wired right now...as long as FPL power is on. There is Generator feeding the building downstairs, but does not feed the MRI off service.....it is located in an meter room on that floor and feed from an MDP downstairs in the Main Electric Room.
This 480V Panel feeds two 3 phase rooftop Chillers and one MRI machine/equipment. The power company has lost B phase to this building's service 4 or 5 times recently.......each time this has happened the Transformer shakes so loud that no one can speak in the office. It has also caused the Equipment ground terminated in the 208V MDP to burn back the insulation. Each time this has happened the people in the office have turned off the Breaker feeding the transformer until the power company fixed it's problem. Then restarting the TX with no issues.
I am planning to install a new 208V primary to 277/480V secondary transformer to at least have the properly rated equipment.......my question is if anyone can lend me some advice as to why the transformer shakes so badly when a phase is lost and why would the equipment ground be carrying amperage and melting under this condition? Is the XO termination lost when the one phase is missing (it typically has been B phase by the way)....My guess is the Neutral feeding the 480V panel from the 208V XO has to be the root of the problem, but I do not know why.