Never say never. If it's a three phase autotransformer the neutral passes through and is common to both sides.
It's a delta wye, there is no neutral that passes through.
Never say never. If it's a three phase autotransformer the neutral passes through and is common to both sides.
I doubt the burned Xo, the noise, with a missing input phase has ANY THING to do with tying Xo to the 480 side:
I doubt the burned Xo, the noise, with a missing input phase has ANY THING to do with tying Xo to the 480 side: I bet these issues were caused by 2 phases on primary trying to power 3 balanced phases of secondary load - that required a real Xo.
I disagree, I have had co-workers have the same issue for the same reason. Not only did the OP state the XO is tied to the load it is also grounded to the frame. You could not burn up XO with out it being connected to ground.
This keeps coming back up every time someone grounds (or connects to neutral) the primary X/H0 terminal.
The delta winding forces the voltages (phasors) AB, BC, and CA to form a closed triangle.
That imposes the exact same equality condition on AN + BN + CN.
During a phase loss that equation cannot be satisfied on the primary side and enormous currents will flow in the 0 terminal trying to make the voltages equalize.
It can even cause large problems without a phase loss if the supply voltages are even slightly unbalanced for any reason.
Sent from my XT1585 using Tapatalk
Exactly what happens here.....
Once FPL loses any phase, the unbalanced load created by the lost phase is trying to get back to its source......which is the Neutral wire from the 480 volt panel which is lost because it's connected to the Low side XO. The current cannot get anywhere so it goes thru the Equipment Ground run with the 208V feeder.........which is terminated on the 208V MDP ground bar......this connection is the weakest point so this is where the massive current is over heating the insulation and burning the wire back.
WRONG. PLEASE reread my last post and Digger's last post. Your statement above is 100% incorrect.
I PROVED to you there is not a return path for current out of your 480v secondary into the Xo. None. Zip. Zilch. Your 480V is NOT AFFECTING ANYTHING HAPPENING ON THE Xo line from your primary. TOTALLY SEPARATE. ISOLATED.
Said another way, your Xo line into your 480v chiller/mri is NOT AFFECTING ANYTHING HAPPENING ON THE 480V side.
We never said that there was not current from X0 to ground and from there back to the utility transformer secondary neutral.Strange that in the cases I know of the conductor bonding XO to ground melted down not the terminal.
You have proved nothing to me.
We never said that there was not current from X0 to ground and from there back to the utility transformer secondary neutral.
But the reason for the current is simply the existence of the delta secondary, not the presence of any kind of loads on it.
In addition to the circulating primary current there will be similarly high currents in the delta windings themselves.
The conductor probably fails because it is undersized relative to the well heat sinked terminal and secondary conductor.
Sent from my XT1585 using Tapatalk
And I am not particularly concerned about proving anything to you, just stating the facts.
Sent from my XT1585 using Tapatalk
WRONG. PLEASE reread my last post and Digger's last post. Your statement above is 100% incorrect.
I PROVED to you there is not a return path for current out of your 480v secondary into the Xo. None. Zip. Zilch. Your 480V is NOT AFFECTING ANYTHING HAPPENING ON THE Xo line from your primary. TOTALLY SEPARATE. ISOLATED.
Said another way, your Xo line into your 480v chiller/mri is NOT AFFECTING ANYTHING HAPPENING ON THE 480V side.
Digger just explained to you why your Xo terminal overheated & why your transformer became very upset and buzzed and shook at you: it is 100% due to unbalanced primary currents trying to still supply 3 secondary windings with balanced loads. Nothing at all to do with the 480v side!
I hope the replacement transformer arrives tomorrow as promised so you get a REAL Xo before someone is hurt!
We never said that there was not current from X0 to ground and from there back to the utility transformer secondary neutral.
Mike seems to be saying exactly that.
Sorry for apparent confusion on my post.
I did NOT say that.
I was simply saying what digger came back and explained: a major imbalance on the input to the transformer caused the Xo hi current - BACK TO THE UTILITY - NOT to the secondary!!!!
I have tried to be clear as mud: there is absolutely ZERO current flow from the 480v secondary windings to the Xo described in the OP.
I am not sure how to say this more clearly.
If I am wrong, OK - prove me wrong. But please do not misunderstand what I wrote and drew a picture of, and assign different meaning to my post..
Whatever ....
It happened and I am dealing with it. So please do not treat me as if I am a simpleton for not completely understanding all of your explanations. I came here for info.....not to be put down and ridiculed for what happened.
Kind of skimmed through and didn't thoroughly read the last 10-15 posts at this point, but the X0 should not be connected when "backfeeding" such a transformer and if that would have been done many of the problems you are having would disappear.I understand there is no current flow from the 480 winding's back to the Utility.....I stated it wrong earlier I know....I was trying to refer that wherever the imbalance was coming from that it was making it back to my EG at the MDP and failing that wire....
The phase imbalance is coming thru the XO wire we ran to the TX frame connection and back through my 208V, line side, equipment ground where it's over heating at it's termination......