480V SWGR MCB TRIP?

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Last night, we had three MCBs trip at the same time on 480V switchgear located in different buildings. The protective relays, ie SEL-751, showed no indication of spikes or surges (also no SPDs are installed at the 480V).
Any ideas what could have caused the MCBS to open?


Sent from my iPhone using Tapatalk
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Opening is not the same as tripping.
Your relays have a history file. You need to look at it.
Investigate the tripping logic equation.

For some reason when there are site wide power losses the POCO initially claims they didn't see anything. They seem to first want you to prove it wasn't you before they look at their system.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Do they have phase loss relays in them? I have seen gear with that option in older buildings. The utility may have lost a phase, causing the main to trip protecting the three phase loads.
The OP relays have almost every function you could want for main/feeder protection. Their trip equation defines which functions actually trip the breaker and when.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Yes, SEL-751s keep a log of the last 8 to 44 trip events, depending on how log (in cycles) the even lasted. In the manual, it's called a "Sequential Event Recorder".

Jraef would it make sense to “extend” the cycles to allow more ride through during surges and spikes?


Sent from my iPhone using Tapatalk
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Jraef would it make sense to “extend” the cycles to allow more ride through during surges and spikes?


Sent from my iPhone using Tapatalk
Only if you know you are tripping on these events.
What does your trip equation say? Are the surge and spikes events which are acted on?

The cycles Jraef was talking about, deal with how much memory is being used by the events recorder not the tripping. Most events occur in just a few cycles, so no changes are needed. There are some events, like swells and sags, which occur over a longer period and so need more recorder memory.
 