Smash
Senior Member
- Location
- Philadelphia suburbs, PA USA
I’m giving an estimate on some 3phase work. There in coming service is 3ph 4w 240V they had a massive bead blast booth installed which they have not run yet. Some one before me installed a 45kva transformer to make the 480V everything looked fine it was bonded had the right size feeders no problem. On my way out I wanted to check the 480V at the blaster disconnect. It’s reading like a ungrounded corner tap delta system
line one 480V to grd line two 480V to grd line 3 0V to ground 480V between all legs is that transformer not wired correctly or does this have something to do with the incoming power. Never came across this before. I want to make sure they did this right before this 50K blaster gets fired up. Transformer reads 208/120 sec 480V primary
line one 480V to grd line two 480V to grd line 3 0V to ground 480V between all legs is that transformer not wired correctly or does this have something to do with the incoming power. Never came across this before. I want to make sure they did this right before this 50K blaster gets fired up. Transformer reads 208/120 sec 480V primary