Issues to consider:
(4) It is normal for a 600Vdc system to be used for a 208 or 240V AC connection. At 480V, a 1000Vdc system is used. For a 1500Vdc system, they often operate at 600Vac. Check the voltage rating of the array, the modules are 600Vdc rated, stick with a 208/240V inverter and skip the transformer.
(5) An autotransformer is YGyg and has a smaller core so core loss goes down. A good choice if you must use 480V inverters on a 208V service.
FWIW, fronius 208 inverters, and even their 240 single phase ones, do 1kv strings.