We are designing for the connection of a 5HP well pump with a factory attached cable for power, thermals of some sort, and for level sensor. The well pump controller is located in a water system vault about 75' away. Originally we had a disconnect for power and 2 jb's for signals at the well head where we converted from factory cable to hard wired. This is because NEC article 400, specifically 400.8.6 which says the cord can't be installed in raceway. However, we have been asked to remove the disconnect and put the splices in a handhole because it is in a public area.
Therefore, we use the NEC exception to eliminate the local disconnect and have a lockable controller main disconnect. We will then have a handhole at the well head for the splices. My question, is we will still need to put the factory cabling in some form of conduit to get from the well head into the handhole, maybe 5' or so. Is this still a violation of 400.8.6? If so, I don't see any other practical way of doing it. How is this typically done?
Somebody may question me, if we allow the factory attached cable to be installed in raceway the 5' between well and handhole, why not just run the factory cable the 75' to the vault. What would I respond?
Therefore, we use the NEC exception to eliminate the local disconnect and have a lockable controller main disconnect. We will then have a handhole at the well head for the splices. My question, is we will still need to put the factory cabling in some form of conduit to get from the well head into the handhole, maybe 5' or so. Is this still a violation of 400.8.6? If so, I don't see any other practical way of doing it. How is this typically done?
Somebody may question me, if we allow the factory attached cable to be installed in raceway the 5' between well and handhole, why not just run the factory cable the 75' to the vault. What would I respond?