160V phase to neutral, then? How weird.Yup. The source may or may not have a neutral, but the motor does not use it.
160V phase to neutral, then? How weird.Yup. The source may or may not have a neutral, but the motor does not use it.
Totally. That is why Jraef stated that what they really mean is that in the US you cannot actually use delta!160V phase to neutral, then? How weird.
Italian motors....arrgghhh! There should be a ban on importing them.Most likely this is a Bonfiglioli (assuming so, because you said Italy) IEC motor that was originally DESIGNED to be used at 400V 50Hz when connected in Wye, then 230V 50Hz when connected in Delta. When connected in Wye, the V/Hz ratio of the motor is 8:1 (400/50). If you apply 480V 60Hz to is, the V/Hz ratio is still 8:1, so the motor will put out rated torque all day, every day, no problem. It will of course turn 20% faster.
But when Bonfiglioli gets the motor listed and labeled in North America, they sell it as a 480V rated motor. Then, BECAUSE people here might THINK it can also be connected to 230V, they explicitly make the nameplate say "277V" if connected in Delta, that way they will think twice about connecting it to 240V 60Hz, which would make it burn up.
So technically the motor is rated 480Y, 277V Delta, but not because anyone can USE it at 277V 3 phase since that doesn't exist. It just says that so that you know you CANNOT use it at anything but 480V when connected to a 60Hz system.
Rated torque and 20% faster would result in 20% more power.Most likely this is a Bonfiglioli (assuming so, because you said Italy) IEC motor that was originally DESIGNED to be used at 400V 50Hz when connected in Wye, then 230V 50Hz when connected in Delta. When connected in Wye, the V/Hz ratio of the motor is 8:1 (400/50). If you apply 480V 60Hz to is, the V/Hz ratio is still 8:1, so the motor will put out rated torque all day, every day, no problem. It will of course turn 20% faster.
We are not talking about delta as applied to the power supply. We are talking about connecting the motor windings in a delta configuration. As Jeff said there is no standard wiring system that will supply 277 volts line to line, but that is what this motor would require if you the motor in a delta configuration.I don't know from motors, but what does 277V delta mean? Three phase, three wires (no neutral) with 277V phase to phase?
I have no idea where you guys are getting this cannot be wired 277 delta. It is a connection configuration and has nothing to do with the source having to be 277 delta. As I've been saying all along, it's simply the same connection as 480 wye, except you connect a 480/277V 3Ø 4W neutral to the joined leads (i.e. optional; also unnecessary in the vast number of cases). It amounts to wiring each motor winding with 277V either way with wye having a floating neutral point, delta not.... As Jeff said there is no standard wiring system that will supply 277 volts line to line, but that is what this motor would require if you the motor in a delta configuration.
And when you connect the windings in delta, you end up with 3 points to connect the power supply wires. What standard power system will give you 277 volts line to line?When each lead is brought out independently (and for reference, we are talking about a six-lead 3Ø motor), all that matters to the motor is the voltage, hertz, and phase relationships of each winding supply.
This is just going around in circles with conjecture and supposition.
A picture of the motor plate will settle matters.
Trying to make sure I understand....You are saying L1 to T1, L2 to T2, L3 to T3, Neutral to 4,5,6. Is that correct?I have no idea where you guys are getting this cannot be wired 277 delta. It is a connection configuration and has nothing to do with the source having to be 277 delta. As I've been saying all along, it's simply the same connection as 480 wye, except you connect a 480/277V 3Ø 4W neutral to the joined leads.....
With independent leads, I'm just trying to point out what is depicted in the following diagram:And when you connect the windings in delta, you end up with 3 points to connect the power supply wires. What standard power system will give you 277 volts line to line?
 
	See my previous post.Trying to make sure I understand....You are saying L1 to T1, L2 to T2, L3 to T3, Neutral to 4,5,6. Is that correct?
But it is never really 480V. It is 277 winding voltage derived from a 480V 3Ø connection.That would give you 277V to the windings but they will still be configured for a 480V connection so the motor is not going to be happy.
That's a star connection disguised as a triangle.With independent leads, I'm just trying to point out what is depicted in the following diagram:

As stated in post #28...That's a star connection disguised as a triangle.
When each lead is brought out independently (and for reference, we are talking about a six-lead 3Ø motor), all that matters to the motor is the voltage, hertz, and phase relationships of each winding supply.
Pictures help.As stated in post #28...
Most likely this is a Bonfiglioli (assuming so, because you said Italy) IEC motor that was originally DESIGNED to be used at 400V 50Hz when connected in Wye, then 230V 50Hz when connected in Delta. When connected in Wye, the V/Hz ratio of the motor is 8:1 (400/50). If you apply 480V 60Hz to is, the V/Hz ratio is still 8:1, so the motor will put out rated torque all day, every day, no problem. It will of course turn 20% faster.
But when Bonfiglioli gets the motor listed and labeled in North America, they sell it as a 480V rated motor. Then, BECAUSE people here might THINK it can also be connected to 230V, they explicitly make the nameplate say "277V" if connected in Delta, that way they will think twice about connecting it to 240V 60Hz, which would make it burn up.
So technically the motor is rated 480Y, 277V Delta, but not because anyone can USE it at 277V 3 phase since that doesn't exist. It just says that so that you know you CANNOT use it at anything but 480V when connected to a 60Hz system.
To just run, sure. You can always run an unloaded motor on lower voltage, but to run right and do the work it's supposed to do voltage has to be right for the way the windings are configured.When each lead is brought out independently (and for reference, we are talking about a six-lead 3Ø motor), all that matters to the motor is the voltage, hertz, and phase relationships of each winding supply.
 
				