solarken
NABCEP PVIP
- Location
- Hudson, OH, USA
- Occupation
- Solar Design and Installation Professional
I am working with a commercial customer to solve some problems with their current service as well as lower their energy costs by installing Grid-tied solar. After monitoring their service through numerous adverse events and damaged equipment, I believe we have convinced them that the root of most of their problems is the open delta 240V service and that it needs to be changed. I would like to ask for any opinions on which service to go to, and any thoughts on pros and cons in making the choice. They currently have 400A service for their 3-phase equipment, open Delta 240V, and a separate 200A service for their single-phase loads like outlets,lighting, and office area appliances. The kWh usage is pretty equal across both services. A few of their machines have transformers that can be rewired to work with 208 or 480 Y. Some machines can operate off 208 as is with no changes. A few machines are designed for 480 but have transformers to convert to the existing 240 Delta.
The decisions to be made:
Change 240 Open Delta to 480Y or 208Y?
collapse their single phase service into the new 3-phase service, Yes or No?
Since the customer has been thru hell the last few years with blown SPD's, damaged machine controls, and downtime after voltage excursions and phase loss events, what protective equipment should we plan to included if any for the new service? Obviously cost is a consideration, but also reliability and resolving their power quality/reliability issues is very important.
Any advice, insight, or suggestions about other things I need to consider are appreciated.
480Y would be better for soalr inverter selection but I want to make the best recommendation for the customer.
The decisions to be made:
Change 240 Open Delta to 480Y or 208Y?
collapse their single phase service into the new 3-phase service, Yes or No?
Since the customer has been thru hell the last few years with blown SPD's, damaged machine controls, and downtime after voltage excursions and phase loss events, what protective equipment should we plan to included if any for the new service? Obviously cost is a consideration, but also reliability and resolving their power quality/reliability issues is very important.
Any advice, insight, or suggestions about other things I need to consider are appreciated.
480Y would be better for soalr inverter selection but I want to make the best recommendation for the customer.