Bjorn Larsen
Member
- Location
- Seattle Area
What is the conversion to properly size the AC side of a -48vdc system that needs 250 Amps?
Transformer rectifier system?What is the conversion to properly size the AC side of a -48vdc system that needs 250 Amps?
I design/build a lot of these plants but do not understand what you are asking.What is the conversion to properly size the AC side of a -48vdc system that needs 250 Amps?
All depends on the size of the rectifier you select. For example if you select a 300-amp @ 48 volt with 110% current limit at 208 3 phase input you are looking at a 50 amp circuit.I have been asked supply a 250A DC load with AC. I will be using 120/208 3-phase as the input.