Fluke 87 or equavalentHighWirey said:Regardless of his test points, exactly what type instrument did Mr Nortel use to determine that you were not within his parameters?
carl
iwire said:If sensitive electronic equipment needs a low ground resistance to operate that must be a bear to achieve in this type of occupancy (Tip of the hat to Bennie)
Would a better description of what sensitive electronic equipment needs to operate properly be 'effective bonding of all non-current carrying metallic objects?'
ELA said:Often equipment manufacturers say they want a low resistance ground. Not necessarily because the equipment itself requires this to operate properly, but what they want is a equipotential ground.
Because NEC requires all equipment to be connected to ground for safety this interconnection can introduce problems between equipments that share grounds.
In the EMC consulting world they refer to ground as the sewer system of electronics. All kinds of higher frequency noise can be dumped onto the grounding system by various equipment. EMI filters dump high frequency to ground. When equipments are tied together through a common ground - high frequency noise currents can cause issues.
Excluding lightning and 60hz safety, what is more important is a zero potential ground plane between interconnected equipments than the actual connection to earth.
Every swicthing and transmission equipment manufacture has a 5-ohm requirement. Problem is very few to none of them know why or can explain it.jghrist said:There is a 5 ohm ground resistance requirement in the Motorola R-56 grounding standard for communications sites.
Frenetic said:But, in regards to safety (around high voltage equipment like at a substation), low impedance is actually very desirable and there is a good reasoning behind this principal. Often times the desired impedance is much lower than 5 Ohms if you can believe that..
Frenetic said:Most of the numbers being quoted by people in reference to impedance come from the NEC or IEEE and frankly, as you mentioned, the reasoning is somewhat limited. People tend to regurgitate what they read so that’s why there’s such a prevalence of these numbers floating around and people not really knowing the reasoning behind them. Also, while the IEEE does indeed have listed numbers, they do in fact try and avoid “firm” numbers in regards to grounding and instead try to emphasis good engineering practice when it comes to grounding..
Huh?tryinghard said:A parallel neutral path does exist between the service source and the service disconnect of every building/structure with a grounded system. Any branch circuitry or feeders downstream from the main that have bonding between neutral and ground (intentional/unintentional) will also have parallel current according to its resistance, returning neutral current travels all paths to source not just the path of least resistance. I think this is the biggest contributor to stray current.
Earth is not a path for fault current or a neutral return path but is a path for static, but so can the branch circuitry EGC if the system is installed correctly.
dereckbc said:What is more important is all the various ground systems involved in a communication system (GES, AC, DC, LPS, Surge Protection, Signal Reference, etc…) is designed and integrated to work with each other to offer the maximum protection that can be afforded.
Dereck
ELA said:Huh?
And you quoted me ... why?
Not necessarily so because most of your modern electronic equipment has components like capacitors, MOV?s etc connected line-to-ground as filters and TVSS which inject current.tryinghard said:If 250-24(A)(5), 250-142(B) are respected current will nearly be eliminated on bonded [grounded] conductive materials. And if the neutral (grounded conductor) was not required to be bonded at the service equipment (250-24(C)), but only at the serving source then isolated thereafter, current on grounded conductive materials would be gone.
dereckbc said:Not necessarily so because most of your modern electronic equipment has components like capacitors, MOV’s etc connected line-to-ground as filters and TVSS which inject current...
tryinghard said:I just expanded with your thoughts that current can/does exist on grounds. You have an interesting post; I would wonder if a zero potential ground could ever be achieved?
Kid I don't think we are talking the same thing here. We are discussing earth impedance where as I think you miight be talking cable impdeance.kid_stevens said:5 ohms is getting off light. In the Navy my electronic and electrical systems had to be .2 ohms to the bulkhead connector and no more than 2 ohms to the Generator ground point.
kid_stevens said:Yep ground or ship hull and deck not cable so after the .2 came off the cable we had to get down to 2 ohms to the Genset ground rod or hull ground point. Granted on shore the genset could get moved closer but we had to salt the ground to make the requirement.