jcook980 said:But if metallic raceways are properly installed and large enough to handle the ground fault current, the internal EGC is not required by the NEC because the conduit is the EGC. Again, 250.122(F) requires that an individual EGC be sized per Table 250.122, where used.
In the case of a metal conduit run I agree with you.
I can certainly leave the EGC out of the conduit and .122(F) does not have any consequence.
If I was to install and connect an EGC in this conduit run than .122(F) comes in.
But this thread is not about a conduit run, this thread is about an MC cable assembly.
IMO with a cable assembly 300.3(B) forces us to use the EGC internal to the MC. Now that it is used .122(F) comes in and forces the use of EGCs based on the OCPD.
Certainly the cable tray can be used in addition to the MCs internal EGC but not in place of the internal EGC.
Perhaps I am wrong about the NEC requirements here, as 300.3(B) has wiggle room, it would be interesting to see some CMP comments about this section.