What you guys usually charge for wiring a 5 Ton A/C, with fusable Disco 40' from panel and air handler 25' from panel?(Of course with emergency switch included) All accesible for wiring. Thanks
You could use #10 (except TW or UF) and a 50-amp breaker, believe it or not.mtnelectrical said:Well its 31.5 Amps circuit with max 50 Amps breaker on nameplate, I am running 8 Ga and 40 Amps breaker, . . .
LarryFine said:You could use #10 (except TW or UF) and a 50-amp breaker, believe it or not.
Make sure the panel will accept and is rated for tandem breakers. The onus is on you to prove that it is. I got knocked down in Ridgewood for this not too long ago. The HO had already installed tandems and I added to them but ended up installing a sub-panel and removing his tandems so I could pass inspection.mtnelectrical said:There is no room for a/c compressor breaker so I am changing 2 breaker with the tandem type to have room for my double pole.
Do you mean outside the house and within the whip to the condenser or inside the house to the disconnect ? Please explain.infinity said:You couldn't use NM either.
goldstar said:.Do you mean outside the house and within the whip to the condenser or inside the house to the disconnect ? Please explain.
goldstar said:If you strip the jacket off NM cable, what is the type of insulation and rating of the conductors inside ? I always thought it was THHN and 90 degrees. Am I wrong ?