Are we required per NEC to have 50/51 G on every breaker that is greater or equal to 1200A per NEC or is it only for service disconnect?
Instantaneous and time-overcurrent ground relay.What is 50/51G?
What is 50/51G?
210.13 Ground-Fault Protection of Equipment. Each branchcircuit
disconnect rated 1000 A or more and installed on solidly
grounded wye electrical systems of more than 150 volts to
ground, but not exceeding 600 volts phase-to-phase, shall be
provided with ground-fault protection of equipment in accordance
with the provisions of 230.95.
215.10 Ground-Fault Protection of Equipment. Each feeder
disconnect rated 1000 amperes or more and installed on solidly
grounded wye electrical systems of more than 150 volts to
ground, but not exceeding 600 volts phase-to-phase, shall be
provided with ground-fault protection of equipment in accordance
with the provisions of 230.95.
230.95 Ground-Fault Protection of Equipment. Ground-fault
protection of equipment shall be provided for solidly grounded
wye electric services of more than 150 volts to ground but not
exceeding 1000 volts phase-to-phase for each service disconnect
rated 1000 amperes or more.
The smart-ass answer would be “No” because it’s 1000A, not 1200A...Are we required per NEC to have 50/51 G on every breaker that is greater or equal to 1200A per NEC or is it only for service disconnect?
So what do you think?
BTW, it says 1000 A in these provisions, not 1200 A.