I think the problem is really with poorly terminated AL wiring when it gets heavily loaded, it has nothing to do with the load being an EV, RV, welder, range, oven, pottery kiln / whatever.
We have seen reoccurring problems here with aluminum wire and the standard 50A range receptacles here in a large multi unit complex, I suspected it was because the installer did not use noalox grease, arguably it was not required.
The units with copper THHN wire and had the same receptacles and have no issues.
All the new 'heavy duty' EV receptacles say CU wire only, which again points to poorly done AL terminations being the real issue.