Ignoring everything but the above, the answer is NO.TSET said:... is it allowable to use copper 8-3 NM cable for 50 amp...
TSET said:The manufacturer has specified 8-3 in the drawing, if under 100 ft.
I'm downloading the PDF nowceltic said:Was 8/3 NM specied...or was #8 minimum (with no wiring method) specified?
By tomorrow morning, you'll have forgotten all about it. Water off a duck's back, brother.QES said:that was unprofessional of celtic to tell other be ignored. We are all professional in here.
HUH?QES said:that was unprofessional of celtic to tell other be ignored. We are all professional in here.
TSET said:Ignoring the question of voltage drop, is it allowable to use copper 8-3 NM cable for 50 amp spa panel feeders, or is the heater question a factor, increasing the cable size to 6-3 (125%)?
The manufacturer has specified 8-3 in the drawing, if under 100 ft.
TSET said:... is it allowable to use copper 8-3 NM cable for 50 amp ...
celtic said:Ignoring everything but the above, the answer is NO.
celtic said:Ignoring everything but the above, the answer is NO.
334.80 ~ 310.16.
60? column as marc stated.
A #8NM has an ampacity of 40A.
No! NM cable is always sized from the 60 degree column, regardless of the terminal rating.TSET said:While it may not be safe for me to assume that the terminals are so rated, based on some small print in an install diagram, do I otherwise have my facts correct?
Link please?TSET said:I'm downloading the PDF now
TSET said:Based on the rule of thumb, as I understand it, you size your conductors in the 60 c column under 100 amps, unless you know the the equipment terminals are rated for 75 c, and then the 75 c column becomes available to size your conductors. While it may not be safe for me to assume that the terminals are so rated, based on some small print in an install diagram, do I otherwise have my facts correct?
TSET said:Celtic,
... Thank you for answering my question.
QES said:equipment terminals will be in effect from main all the way to spa? or just just spa panel to spa?
110.14(C) Temperature Limitations.
The temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device. Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both.
From the Olympic Spa website:celtic said:On the install instructions....was it #8 NM or just #8?
230 VOLT SUBPANEL WIRING INSTRUCTIONS
NOTE: The subpanel must be placed within 100 feet of the main electrical service panel, and between 5 (1.5 m) and 50 feet (15 m) away from the
spa. All electrical connections must be made in accordance with the wiring information contained in this manual and on the back of the field wiring
access panel of the control box.
Refer to the wiring diagram below.
1. Connect the #8 AWG, WHITE [NEUTRAL] wire from the Neutral/Ground Bar on the main electrical service to the WHITE [NEUTRAL, Panel
Neutral, Pigtail] of the subpanel.
2. Connect the #8 AWG, BLACK [L1] wire from the main electrical service to the subpanel [terminal L1].
3. Connect the #8 AWG, RED [L2] wire from the main electrical service to the subpanel [terminal L2].
4. Connect the #10 AWG, GREEN wire from the Neutral/Ground Bar on the main electrical service to the GROUND terminal of the subpanel.
5. Connect the #8 AWG, WHITE [NEUTRAL] wire from the subpanel breaker to the Neutral terminal on the spa?s control box.
6. Connect the #8 AWG, BLACK [L1] wire from the subpanel breaker to terminal [L1] on the spa?s control box.
7. Connect the #8 AWG, RED [L2] wire from the subpanel breaker to terminal [L2] on the spa?s control box.
8. Connect the #8 AWG, GREEN wire from the GROUND terminal of the subpanel to the GROUND terminal in the spa?s control box.
9. Bond the spa to all exposed metal equipment or fixtures, handrails, and concrete pad pre N.E.C. and all local codes.