080630-1128 EST
Tony:
Can you provide a better discription of the power part of the circuit? Why was the switching supply mentioned if it does not relate to the power to the resistive load?
Reading back thru your posts I find that you may be saying that there is a 220 V 50 Hz AC supply, a Triac, and a resistive heater load that I now assume are in a series loop with no other components in that loop.
Most heating elements will have a thermal time constant longer than 1/60 or 1/50 second and therefore should not care whether it is 60 or 50 Hz.
Suppose the Triac remained on continuously, then would the heater fail? If not then you have an environmental problem if the voltage does not go above whatever maximum voltage the heater can continuously tolerate.
Next assume the design was not that conservative. Is this a bang-bang, or a phase modulation servo system? May not be important but would be useful to know. In either case if the controller failed for a short time and kept the Triac on, then the heater could burnout.
Assuming ambient temperature is reasonably constant and you do not change the content of whtever is inside of this heater where your temperature sensor is, then there should be no great changes in heater current averaged over a moderately short time period. Any sort of current monitor, average or RMS reading, with a time constant of 100 to 500 MS (a standard analog meter movement or typical digital meter) measuring the heater current should allow you to see if abnormal current changes exist. Obviously it should be a recording meter. Probably a computer with appropriate harware and software.
A bang-bang (on-off) controller might have a longer time constant than the above (100 to 500 MS), but recording the measurements would still allow observation of abnormal conditions.
Consider this example. A system with only temperature monitor and no current monitor, a consrvative design for 220 V such that full on of the heater would not cause burnout, and an assumption input line voltage was moderately constant at 220 V, and a long time constant from heater to temperature sensor such that this time constant is long relative to a burnout time if overvoltage is applied. Now fail the one assumption about line voltage and have a voltage that rises to 1.4 times normal, then power input is doubled and the heater fails.
If the controller loop included current or voltage measurement, then line voltage would have no effect unless it went high enough to fail the Triac.
.