I work for Siemens.
Assuming this is a large contactor, size S6 or greater, it is indeed a little switch mode power supply board and it feeds a PWM signal to the coil. So you can feed it just about anything. 40 to 60Hz AC, even DC if you have to! The voltage tolerance is also extra wide: 70% to 125% of nominal rated voltage. So in your case, 84 to 150V, AC or DC.[/QUOTE
THE PIECE OF EQUIPTMENT THAT I AM WORKING ON IS A TRANE CVHE 450. IT HAS A WESTINGHOUSE EXTERNAL STARTER CABINET,EVERYTHING INSIDE THE CABINET IS WESTINGHOUSE (1M,2M,SHORTING,AND TRANSITION CONTACTORS). THE TRANSITION RESISTORS IN THE PANEL BURNED DUE TO THE (2M )NORMALLY CLOSED AUX. CONTACTS FAILING. DURING TROUBLESHOOTING I FOUND THE BOARD BAD. I THEN STARTED TRYING TO LOCATE PARTS(WESTINGHOUSE HAS BEEN BOUGHT AND SOLD HOW MANY TIMES) TRANE COULDNT OR WOULDNT HELP BECAUSE THERE WERE NO TRANE PART NUMBERS. LOCATING PARTS WAS MURDER ,I HAD TO HAVE THE RESISTOR GRID BUILT, I COULDNT FIND JUST THE BOARD SO I HAD TO BUY THE ONLY NEW 2M CONTACTOR I COULD FIND : AND JUST ANY CONTACTOR THAT FIT THE APPLICATION WOULD NOT WORK DUE TO THE ACCEPTANCE OF AUX. CONTACTS AND A MECHANICAL INTERLOCK. THE ONLY DIFFERENCE IN THE NEW 2M WAS THE P.S.C.B. (50 INSTEAD OF 60). THE VENDOR SAID THE 50HZ C.B. WOULD WORK BUT HE WOULDNT WARRANTY IT IF I POWERED IT WITH 60HZ POWER. NOW YOU KNOW WHY I WAS SKEPTICAL.