i received a violation for having a circuit breaker larger than 50% of the rated mains. Do you know if this is a code requirement or a manufacturers requirement? I cant locate it in my codebook
 
S m

S m

If the mains is rated for 100 Amps, there is no code requirement against using a 50% rated distribution breaker.

The violation can be cited if this breaker were to in a panel where max distribution breaker size is less than this (50 A).

If the issue is anything else please clarify or ask the inspector what NEC code is violated.

Hope this helps

SM
 