hardworkingstiff
Senior Member
- Location
- Wilmington, NC
I am looking at a dock with one section having five 50-amp receptacles not individually metered. 555.12 says I can use a .9 multiplier for service calculations. 250*.9 = 225-amps. 225*240-volts = 54KVA (single-phase) transformer (we are feeding the dock w/480-volts).
Question, transformers go from 50KVA to 75KVA. Do you think 50KVA is OK (I think it's fine)? Do you know if the NEC will allow the 50KVA in this instance (I don't know)?
Thanks,
Question, transformers go from 50KVA to 75KVA. Do you think 50KVA is OK (I think it's fine)? Do you know if the NEC will allow the 50KVA in this instance (I don't know)?
Thanks,