Well, here goes. This is from the 2005 Report on Proposals:
14-24 Log #3328 NEC-P14 (501-4(A)(1)(a))
Final Action: Reject
Submitter: Jon Miller, Detector Electronics Corp.

Recommendation:
Revise text to read as follows:
"...threaded joints shall be made up with at least five three and one half threads fully engaged...".

Substantiation:
Explosion proof/flameproof enclosure threaded entries are required to conform with ANSI/ASME B1.20.1 (Pipe Threads, General Purpose Inch) with modified L1 gauging of +0.5 to +3.5 to ensure a minimum of five full threads engagement. This deeper tapped hole produces an unsafe condition on shouldered fittings when the shoulder is dimensioned at less than L4 producing a condition where the threads do not fully engage. There are currently no standard requirements to address this condition. In addition, this deeper tapped hole of a flameproof enclosure, which may be significantly thinner wall enclosure in comparison to an explosion proof enclosure, in
combination with a threaded blanking element are not able to ensure five full threads engagement under worst case wrench tight conditions. For this reason the International Standard for Type of Protection "d" (IEC 60079-1) requires conformance to ANSI/ASME B1.20.1 (L1 gauging of +/- 1 to ensure a minimum of three and one half full threads engagement) for minimum thread engagement requirements on taper threaded joints. This requires US manufacturers producing a single product for international markets to conform
with L1+0.5 to L1+1 for female taper threaded entries resulting in tight inspection requirements and high scrap potential.

Panel Meeting Action: Reject
Panel Statement:
This issue is considerably more complex than indicated by the proposal. Some of the factors involved include:
- thread gauging of both male and female parts;
- problems with shoulders on the male parts;
- concerns about misapplication during field installation.
The submitter still has not provided sufficient evidence that this reduction in the requirement will provide an equivalent degree of safety.
Number Eligible to Vote: 14
Ballot Results: Affirmative: 13 Negative: 1

Explanation of Negative:
ENGLER: ISA disagrees with the CMP 14 rejection of this proposal based on the following:
The reasons for rejecting the proposal involve issues that can be effectively addressed by the revisions shown below. As the IEC standards are definitely being revised to reflect the "US" NPT gauging practices included in ANSI B 1.20.1, manufacturers will be very negatively impacted if a compromise position cannot be found. Revise indicated sections as shown:
500.8(D) threading. All threaded conduit or fittings referred to herein shall be threaded with a National (American) Standard Pipe Taper (NPT) standard conduit cutting die that provides a taper of 1 in. 16 (3/4-in. taper per ft). Such conduit shall be made wrench tight to prevent sparking when fault current flows through the conduit system and to ensure the explosion proof or flameproof integrity of the conduit system where applicable. Equipment provided with threaded entries for field wiring connections shall be installed in
accordance with 500.8(D)(1) or (D)(2). Threaded joints with field threaded NPT entries shall be made up with at least five threads fully engaged for entries into explosion proof equipment. Threaded joints with factory threaded NPT entries shall be made up with at least 4 1/2 threads fully engaged for entries into explosion proof equipment. Threaded joints with metric entries shall be made up with at least five threads fully engaged for entries into explosion proof equipment.
501.4(A) Class I, Division 1.
(1) General. In Class I, Division 1 locations, the wiring methods in (a) through (d) shall be permitted.
(a) Threaded rigid metal conduit or threaded steel intermediate metal conduit. Threaded joints shall be made up with at lest five threads fully engaged.
505.9(E) Threading. All threaded conduit referred to herein shall be threaded with a National (American) Standard Pipe Taper (NPT) standard conduit cutting die that provides a taper of 1 in. 16 (3/4-in. taper per ft). Such conduit shall be made wrench tight to prevent sparking when fault current flows through the conduit system, and to ensure the explosion proof or flameproof integrity of the conduit system where applicable. Threaded joints with field threaded NPT entries shall be made up with at least five threads fully engaged for entries into flameproof or explosion proof equipment. Threaded joints with factory threaded NPT entries shall be made up with at least 4 1/2 threads fully engaged for entries into flameproof or explosion proof equipment. Threaded joints with metric entries shall be made up with at least five threads fully engaged for entries into explosion proof equipment.
Justification for changes to 500.8(D), 501.4(A) and 505.9(E):
The 5 thread engagement requirement specified within the NEC text should be changed to 4 1/2 thread engagement for alignment with IEC product standard gauging practices for factory NPT threaded joints. This change allows US manufacturer's to gauge NPT entries to a single internationally accepted gauging practice (0 to + 2 turns of L1) rather than the currently restrictive gauging practice (+1/2 to +1 turns of L1).
This comment addresses the issues in the panel statement as follows:

Panel Statement: Issue involves thread gauging of both male and female parts.
Response: Proposed revisions allow "reduced" thread engagement ONLY for joints that include factory threaded entries.

Panel Statement: Issue involves shoulders on male parts.
Response: ISA has submitted parallel proposals for U.S. and IEC product standards to address this issue. The revisions shown above ensure that when male parts with properly located shoulders are installed into factory threaded entries, at least 4 1/2 threads are fully engaged.

Panel Statement: Issue involves concerns about misapplication during field installation.
Response: Revisions above limit reduced engagement allowances to factory threaded entries.

Panel Statement: Submitter has not provided evidence that reduction in the requirement would provide an equivalent level of safety.
Response: It is widely recognized that when both male and female parts are threaded in the field that it is very typical to achieve significantly less than five fully engaged threads. The revisions above reduce the existing requirements by 1/2 threads only when the entry is factory threaded.

Note: Supporting Material available for review at NFPA headquarters.


The proposal is so long, I can't even post the ROC in the same post. :)
 
Last edited:

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
This is from the 2005 Report on Comments:
14-17 Log #481 NEC-P14 Final Action: Accept in Principle( 500.8(D) )
Submitter: Vic Gournas, ISA-The Instrumentation, Systems and Automation Society
Comment on Proposal No: 14-24

Recommendation: 500.8(D) Threading. All threaded conduit or fittings referred to herein shall be threaded with a National (American) Standard Pipe Taper (NPT) standard conduit cutting die that provides a taper of 1 in 16 (3/4-in. taper per foot). Such conduit shall be made wrenchtight to prevent sparking when fault current flows through the conduit system and to ensure the explosionproof or flameproof integrity of the conduit system where applicable. Equipment provided with threaded entries for field wiring connections shall be installed in accordance with 500.8(D)(1) or (D)(2). Threaded joints with field threaded NPT entries shall be made up with at least five threads full engaged for entries into explosionproof equipment. Threaded joints with factory threaded NPT entries shall be made up with at least 4 1/2 threads fully engaged for entries into explosionproof equipment. Threaded joints with metric entries shall be made up with at least five threads fully engaged for entries into explosionproof
equipment.


Substantiation: ISA disagrees with the Code-Making Panel 14 rejection of this proposal based on the following:
The reasons for rejecting the proposal involve issues that can be effectively addressed by the revisions proposed. As the IEC standards are definitely being revised to reflect the ?US? NPT gauging practices included in ANSI B 1.20.1, manufacturers will be very negatively impacted if a compromise position cannot be found.

Justification for changes to NEC 500.8(D), 501.4(A) and 505.9(E):
Reducing the 5 thread engagement requirement specified within the NEC text for factory cut female NPT threads to 4 1/2 thread engagement, allows a more manufacturable product for worldwide use, and better alignment with the IEC product standard gauging practices for NPT threaded joints. This change allows manufacturers to gauge female NPT entries to a gauging practice of (0 to +1 turns of L1) for international use that than the currently restrictive gauging practice (+1/2 to + 1 turns of L1). This proposal will not affect field cut NPT threads, male or female.


Panel Meeting Action: Accept in Principle Revise the proposed text to read:500.8(D) Threading. All NPT threaded conduit and fittings referred to herein shall be threaded with a National (American) Standard Pipe Taper (NPT) thread that provides a taper of 1 in 16 (3/4-in. taper per foot). Conduit and fittings shall be made wrenchtight to prevent sparking when fault current flows through the conduit system, and to ensure the explosionproof integrity of the conduit system where applicable. Equipment provided with threaded entries for field wiring connections shall be installed in accordance with 500.8(D)(1) or (D)(2). Threaded entries into explosionproof equipment shall be made up with at least five threads fully engaged.
Exception: For listed explosionproof equipment, factory threaded NPT entries shall be made up with at least 4 1/2 threads fully engaged.
Panel Statement: The panel agrees with the submitter's substantiation but has limited its application to listed equipment with NPT threads only. The panel is concerned that there is less control over field installed-threads and thus has not extended the 4 1/2 thread provision to those installations. In addition, metric entries have not been included in this exception, as they are not tapered threads. These changes do not modify the requirement that threaded joints be made up wrenchtight.


Number Eligible to Vote: 15
Ballot Results: Affirmative: 12 Negative: 3

Explanation of Negative: BRIESCH: The panel action should be to reject this comment and retain the requirement for 5 full thread engagement. This proposal is in direct conflict with ANSI requirements for both threading and gauging of NPT threads for not only hazardous locations electrical fittings, but general purpose electrical fittings, boxes and enclosures.
NPT electrical conduit and fitting threading and gauging practice is harmonized in ANSI/NEMA FB-1, ANSI/UL 1203, ANSI/UL 514A, ANSI/UL 50, ANSI/UL 6 and CSA C22.2 No. 0.5. A correctly formed NPT male thread will end a distance of L4 from the end of the conduit or fitting plus or minus the 1 turn gauging tolerance allowed by the standard. Obtaining 5 thread engagement of the female and male tapered NPT threads depends upon the correct thickness of the female wall for the thread pitch involved, the length of the threaded male fitting and forming the threads correctly to achieve the desired engagement. North American electrical fitting NPT thread forms are required by the above standards to be formed in a manner such that not less than 5 full threads can be achieved upon wrench-tight engagement. In the worst case, the female entry gauged at +1/2 and a male part gauged at -1 and made wrench-tight will engage 5 threads. It should be noted that there are requirements for general purpose boxes and enclosures that require 5 threads in the female entry in UL 514A, UL 50 and NEMA FB-1. It should also be noted that installation documents are currently globally harmonized at 5 full threads engagement for explosionproof and flameproof tapered entry threads.

COOK: Based on the substantiation provided in Comment 14-23, it appears that this action would allow a product to be installed in a hazardous (classified) location that would not meet the product standards for ordinary locations.

WIRFS: Mr. Briesch and Mr. Cook have pointed out compelling substantiation to maintain the full five-thread engagement requirements and consistency with a large base of manufacturing standards. Until there is further substantiation to modify this requirement in a manner consistent with those standards, it should not be changed in the NEC
.

Near as I can figure, from scanning this, the ISA convinced the Code Making Panel that listed equipment can be trusted at 4.5 threads.

I'll let you read this and tell me what it actually says. :)
 

travis301

Member
Location
Missouri
Long story short:
If I am going into a factory threaded device such as a box or a fitting,I need 4 1/2 threads.
If I am going into a field threaded entry I need 5. What would a field threaded device be other than the threads I made on the conduit? Are they talking about if I tap a hole into the side of an explosionproof box?
 