500 amp breaker upstream of another 500 amp?

Status
Not open for further replies.
We have an existing 500amp breaker service disconnect inside a building (correctly sized for the loads). We want to install a new service disconnect outside the building upstream of that. Can we use another 500 amp breaker disconnect to avoid upgrading the wiring to the existing disconnect?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Sure you can. But you will need to relocate the N-G bond to the outdoor disconnect, and include an EGC in the cable to the inside disconnect.
 