Luketrician

Senior Member
Location
West Pawtucket
zog said:
I think the 10 Ft distance is for qualified personel working on equipment in section 1910.269, the 25 ft is for unqualified personel. From the sounds of it the OP is working on equipment described in 269 but is unqualified based on the fact that the OP had to ask the question in the first place.[/QUOTE]


I addressed that already in post 12 and 17. Before I even started this thread I knew that the minimum distance was around eleven feet~ but like I have already stated I am not a lineman and since I don't work around 500kv everyday I certainly cannot know exactly what is and isn't safe without doing a little research.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Marc,
Yes the lights are equipment, but they are not generation, control, transformation, transmission or distribution equipment. In my opinion the lights do not fall under that standard.
Don
 

djohns6

Senior Member
Location
Louisiana
I don't know if this will make you feel any better , but that 500kv is a phase to phase voltage . Phase to ground will be in the neighborhood of 289 kv .
 

Luketrician

Senior Member
Location
West Pawtucket
djohns6 said:
I don't know if this will make you feel any better , but that 500kv is a phase to phase voltage . Phase to ground will be in the neighborhood of 289 kv .



Oh ok, I did not know that. I do feel alot better though. Were done re-lamping now and next week we will start changing out ballasts in some of the fixtures.

Thanks for all of the positive, helpfull replies.:smile:
 

zog

Senior Member
Location
Charlotte, NC
djohns6 said:
I don't know if this will make you feel any better , but that 500kv is a phase to phase voltage . Phase to ground will be in the neighborhood of 289 kv .

Oh, thats nothing (Kidding)

Be careful out there Luke, may the force be with you (Couldnt help that one)
 

WDeanN

Member
Luketrician said:
Oh ok MD, I was thinking that something was amiss here..with there being such a huge gap between TVA and Osha safety procedures....:confused:

Luke,
I worked with the guy that wrote many of the line procedures at TVA for a couple of years. If OSHA is more conservative than TVA, it's because OSHA changed since he retired (about 5 years ago.)

You can also thank him (and partly me, I interned at TVA in Chattanooga) for TVA's arc flash procedure.
 

Luketrician

Senior Member
Location
West Pawtucket
Well then, I will have to say thanks for your time WDeanN. Your time and efforts with TVA help keep me and other electricians out there safe.

Best regards to you Sir.
 