Except that the code requires the EGC be in the same cable.Since you are planning to direct bury 'cables' which are really conductors bundled together without an external sheath, I don't see a problem with just adding the required EGC as single conductor direct bury wire in the same trench.
(1) Paralleled Installations. Conductors shall be permitted to
be run in parallel in accordance with the provisions of
310.10(H). The requirement to run all circuit conductors
within the same raceway, auxiliary gutter, cable tray, trench,
cable, or cord shall apply separately to each portion of the
paralleled installation, and the equipment grounding conductors
shall comply with the provisions of 250.122. Parallel runs
in cable tray shall comply with the provisions of 392.20(C).