Ok, in case I put it ( the solenoid and the valve) inside an enclosure (general purpose or type 4x..etc) then I can use listed fitting with LFMC as an example, is this acceptable???:blink::blink::blink::blink::blink:
There are others on this site that can better tell you what you can do in a
listed manufactured assembly under Section 90.7 for a Class I, Division 2 installation. So far, none of them have challenged my position or suggested that as a solution. I have accepted fully wired factory assembles when all internal wiring is terminated on factory installed terminal blocks and all other internal components are suitable for Division 2. The entire assembly must be suitable [Section 500.8(A)] for Division 2. If the exterior is properly marked by a NRTL (
NOT "CE" marked) for the entire assembly as suitable for Division 2, I probably would accept it without an internal inspection. In over 45 years, I've never seen it. Usually the enclosure is simply marked as a UL 508A Industrial Control
Panel and it doesn't cover the internals as suitable for Division 2. Otherwise, the answer is still
NO; the wiring as shown is still unsuitable for Division 2, enclosed as suggested or not.
That said, enclosing everything may also open this to a purged/pressurized solution if the entire assembly isn't otherwise suitable. .[NFPA 496, NEC Section 500.7(D)] A purged/pressurized solution is still an expensive alternative for not getting a proper solenoid.