A customer has requested a 50A 240V (NEMA 14-50) receptacle in an outdoor location for charging his new EV (Tesla Model S).
The "Mobile Connector" (aka cord) that ships with the Model S looks like this (click image for larger version):
Tesla has recommended that an RV outlet could be used.
406.8(B)(2)(a) requires a weatherproof-while-in-use enclosure in wet locations for unattended equipment, and while a typical right-angle RV plug would allow the cover of that type of enclosure to close completely while the plug was inserted, the Tesla connector seems like it would prop the cover partially open. Depending on the actual angle that the cover would rest at while in use, it might or might not be a problem for water intrusion...but I can't assess that until I actually plug the connector into the outlet. Even if it's not a problem in "real world use", a partially-open cover might not meet the manufactures requirements for use corresponding to its listing, and I'd rather not ignore those details.
I've seen an "improvised" solution to this problem (pic below was posted in this Tesla owner's forum) and while seeming pretty weatherproof when the cabinet door is closed, I don't think it's legal, for a few reasons. I'd like to know your opinions on WHY it IS, or is NOT, a legal install...and, could a version of this be done that would BE legal?
Thanks, I always appreciate all that I get from this forum...