I'm feeding a 100A main breaker panel from another panel using a 50A breaker. I plan to size the cable based on the source breaker (50A in this case), but I thought there was something in the code that may prohibit this?
Not a problem. Your would not even need a main breaker.
I must be getting confused with another section of the code. For a second I thought that I could do it with the 50A breaker, but would need to run #2 cable. Isn't there something in the code restricting size of cable landing on a breaker? I was thinking I could feed it with the 50A breaker, but would need to size the cable based on 100A..........
Thanks for the response.
Unless the sub-panel is in a separate structure.Not a problem. Your would not even need a main breaker.
Can you tell me where in the code it states that?
It doesn't.
230.71 If the 100 amp panel has more than 6 switches (single or double pole) i.e. breakers, then it needs a main. If equal or less then 6 pole spaces, then no main. Of course, one could install tandem (twins), then non compliant....
So, "it depends".
Well, main or 6-handle limit.Can you tell me where in the code it states that?
Main or 6-handle limit applies in separate structures.You're talking about services, the OP is talking about a subpanel.