tallgirl
Senior Member
- Location
- Glendale, WI
- Occupation
- Controls Systems firmware engineer
I did tell you that I can't comment on code requirements
Well, I sort of need something that's Code compliant ...
So what do you think Variable Frequency Drive actually means?
VFDs do NOT create sine waves.
HTH.
Yes, to feed a motor. But run from output to input does not depend on motor characteristics.
Correct. However, if the output side of a VFD doesn't function pretty much like the electric grid, the inverters won't sync and stay synced. In particular, most UL1741 compliant inverters will try to change the behavior of the "grid" to make sure it really is the grid. If that VFD allows the inverter to change the voltage or frequency (which it likely will) of the "grid" (the VFD output), the inverter wil decide it is islanded and disconnect.
HVDC stuffs oodles of the stuff back into the grid. How bad is that??
And yes, not only will work. It does.
Yes, because they are DESIGNED for the purpose.