Greetings all I am reviewing NEC 514 for some upcoming projects that involve adding a propane filler to a gas station.
This is typically what you refill a RV propane tank, 5 gal BBQ tank, or the rare propane powered vehicle (apparently I am told they exist never seen one)
Its one facility, with say 2 hazardous locations two gas islands now a proposed 3rd (propane filler). The locations dont overlap.
Does the propane filler location need to be tied into the e-stop for the other two?
Or can each have its own e-stop?
From what I have seen in the feild I think the islands (haz locations) each have their own, that are independent.
Reviewing 514.11(A) Circuit Disconnects sentence 3 is making me think current NEC wont allow that and they all get tied together:
locations plural instead of location make me think all the pumps at a site need to be on one e-stop.
Say you had two large gas filling islands on opposite sides of a convenience store and a propane filler a decent distance away from them.
Does the estop typically serve the entire 'Facility'
Thanks in advance
The use of the word All seems like it would include the entire facility.Emergency shutoff devices or electrical disconnects shall disconnect power to all dispensing devices;
to all remote pumps serving the dispensing devices;
to all associated power, control, and signal circuits;
and to all other electrical equipment in the hazardous (classified) locations surrounding the fuel dispensing devices.
When more than one emergency shutoff device or electrical disconnect is provided, all devices shall be interconnected.
Thanks in advance